General Thermography

Emissivity for PdM inspections

 
Picture of Fred Colbert
Emissivity for PdM inspections
by Fred Colbert - Thursday, 30 August 2007, 6:38 PM
 

What is the typical emissivity that you place into your camera when you are conducting for example a infrared electrical inspection of indoor switch gear, or how about outside electrical equipment in a substation?  lets have a discussion about what you think about it?

What emissivity are you using, or what emissivity settings are you seeing other people use, and what is your option?

Speak up...be heard!

Fred Colbert

Picture of Julio Arroyo
Re: Emissivity for PdM inspections
by Julio Arroyo - Thursday, 29 May 2008, 1:31 AM
 

Hi Fred,

I am using infrared electrical inspection emissivity 0,75 (Indoor and outdoor)

Is correct emissivity?

I wait for you answer.

Julio Arroyo

Cámara Flir P65
Re: Emissivity for PdM inspections
by Daniel Enrique Tejeda Alvear - Saturday, 4 October 2008, 9:13 PM
 

Para equipos eléctricos por lo general uso 0.95, pero en realidad para inspecciones termográficas en contactos eléctricos lo importante o lo que nos interesa es detectar donde está el punto caliente anormal y con cualquier emisividad lo puedes hacer. Uso 0.95 porque es la emisividad con la cual puedo obtener datos de temperaturas mas cercanos a los reales, cuando estamos inspeccionando equipos eléctricos nos dirigimos hacia las conexiones en donde hay endiduras u orificios entre contactos y conductores estas asemejan el comportamiento de un cuerpo negro cuya emisividad es igual a 1.